Steel mill keeps its emissions record stainless

Process instrumentation fed by multiple 4-20 mA loops enables mill operator to keep a watchful eye on pollutants

May 2013

FlukePlus member Robert Applegate feels compelled to stay current with process control technology - especially when it may have a direct impact on controlling acid rain and other pollutants. Twenty weeks out of his year are devoted to a high-pressure boiler-emission monitoring system at a northeastern steel mill, where he is a consultant.

At the mill, critical readings about system operations are taken from field instruments connected via 4-20 mA loops and then fed to a central distributed-control system or DCS. Additional DCS loops send control information to the emission monitoring system, enabling the mill operator to verify continued compliance with EPA-mandated requirements. The DCS data, also used for proper/safe boiler operation, is NOT available for troubleshooting/calibration while operating the boiler.

"Given those limitations, I now use a Fluke 771 ClampMeter to investigate the data inputs and compare them with the outputs to the emission monitoring system - without shutting down the boiler." The meter is purpose-built to measure 4-20 mA loops, clamping around a single wire without interrupting the circuit.

It's in the chemistry

What role do low-current loops play in efficiently operating the mill and limiting pollutant levels to abide with the EPA-mandated standard? The mill contains five major boilers whose outputs feed into stacks. The emission-monitoring system extracts continuous stack samples, measuring the nitrous oxide and oxygen concentration levels. "They call nitrous oxide NOx because there is more than one version," says Applegate. "It could be NO, or it could be NO2, and hence the term NOx. NOx is a precursor to a visible haze of pollution, which itself is a precursor to acid rain."

The idea, he says, is that by controlling the admission of NOx and sulfur dioxide, or SO2, mills can lower the concentration of nitric acid and sulfuric acid, or H2SO4 (the result of SO2 combined with water). "That's a major step toward reducing acid rain, which in the eastern US is threatening to devastate major forests," says Applegate.

"This is where 4-20 mA technology comes in, and why it's critical for deriving what we call "emission factor." We look at all the fuels that flow into the boiler, and all the monitoring instruments report their fuel flow rates. Then we take those rates, combine them with the amount of heat present in that fuel, and generate the heat input. Now we have a heat input to the boiler and a steam flow out of the boiler, and we have the concentration in the stack. From those three measurements, we develop the emission factor."

The system determines how much NOx went up the stack in that set of circumstances. Here Applegate points to the critical need for "noninvasive" testing. "The instruments reporting fuel flows are also used to control the boiler, and they have to be calibrated. I can't go out there and say 'I'll just disconnect the oil flow meter and measure the flow.' If I did that, the boiler would trip."

No more shutdowns

At one time, he says, the only way to troubleshoot those instruments was to shut the boilers down - which meant waiting for once- or twice-a-year planned outages. "That meant there were long periods when I couldn't verify what a process control instrument was actually doing - unless I had a tool like the Fluke 771. Now I can go out there, measure the circuit loop between the instrument and the DCS, and say 'Alright, I'm at 55 %.' Now I look at what's coming to the NOx system and verify that it's also 55 %. You can compare the input side to the output side without disconnecting anything."

Percentage readings, he notes, give the technician another way to track critical indicators. A unique feature of the Fluke 771 is its dual readings: milliamps and percent of scale. For example: "A reading of 4 mA equates to zero percent of scale, and a reading of 20 mA equates to 100 %," he says. "In my case, 55 % would give me a reading of 12.8 mA." And how do units of flow equate to currents and percentages? "When you set everything up, you pick a span number. You say the span is going to be full-scale. If it's an oil flow meter, it might be zero to 30 gallons per minute. At 30 gpm, you'd be generating 20 mA, and you'd be looking for 100 % at the DCS level."

He notes that, in the 'DCS world,' readings of all kinds are converted from absolute readings of current between 4 mA and 20 mA, to a percent of some factor. Working with percentages is often easier than keeping current values in mind, while achieving the same results.

"We're using the instrument for dual purposes: One, to monitor the boiler and ensure it's safe for continuous operation, and two, to compare the amount of heat created by the boiler with the gas concentration in the stack. Those numbers calculate the emission factor, which tells us how much NOx the system is generating."

All loops are created equal

Applegate points out an inherent advantage of 4-20 mA technology. "At the mill, a regulator device sources that current. Within limits, it doesn't care whether that loop is 10 feet or 1000 feet long. The current is the same everywhere in the loop. The longer it is, the higher the resistance. But, because it's regulating current, the system just increases the voltage in order to drive the current to the level it wants to be. It's a low-impedance circuit that isn't impacted by noise in the surrounding area. That's because the current is high enough that any noise generated in the proximity of the circuit doesn't compare with the strength of that low-impedance, relatively high-current circuit."

In a sense, 4-20 mA technology is a great equalizer. And that is perhaps why the technology is still used in new industrial systems, even as newer bus technologies have been introduced.

But an enduring technology requires durable, easy-to-use tools. "What I like about the Fluke 771 is that it's uncomplicated," says Applegate. "It's not huge or unwieldy, and it's straightforward to use. A 4-20 mA tester like the Fluke 771 is the kind of tool that everybody in the process control world needs to do this type of work effectively. It's going to be like a flashlight."