English

Reassessing airport tower lightning protection systems

Grounding

Most airport towers are built with Lightning Protection Systems. However, serious incidents do occur.

According to a recent Associated Press story, a lightning strike on the airport tower at Baltimore/Washington International Thurgood Marshall (BWI) Airport injured an air traffic controller and revealed a potential vulnerability that could affect towers at other U.S. airports. In the BWI incident the Lightning Protection System failed, most likely because the cable was cut during a construction project several years earlier.

The air traffic controller is recovering, but the incident was serious enough to prompt the Federal Aviation Administration (FAA) to make plans to assess the Lightning Protection Systems at the 440 U.S. air traffic control towers it managers. Special attention will be focused on the 200+ towers built before 1978, when the FAA first established its lightning protection requirements for the following:

  • airport control towers
  • Navigation and Approach Lighting Systems (ALS), including airport beacon, PAPI, VASI, RAIL, REIL, VOR, ILS, and MALSR systems
  • weather and airport advisory systems, including RVR, ATIS, AWOS, and ASOS
  • high and low voltage electrical and communication cabling systems; fiber optic placement, splicing, and testing; and airport grounding systems

Lightning protection components at a glance

  • An air terminal, down conductor, and at least one ground plate or rod for each beacon tower, should be installed.
  • The air terminal should be installed at the top of the tower with the tip of the rod extending not less than 150 mm (6 in) above the top of the beacon.
  • Down-conductor cables should be securely fastened to the surface of the tower leg at 150 cm (5 ft) intervals with suitable bronze fasteners having bronze or noncorrosive metal bolts. Sharp turns or bends in the down conductor are not permitted.
  • All connections of cable-to-cable, cable-to-air terminals, and cable-to-ground plates or rods must be made with solderless connectors or noncorrosive metal.
  • The down-conductor cable shall be securely attached to ground rods or plates placed at least 60 cm (2 ft) away from the tower foundations. The ground rod shall be driven into the ground so that the top is at least 150 mm (6 in) below grade. The down-conductor shall be firmly attached to the ground plate or rod by means of a ground connector or clamp.

If an airport is located in an area with a high incidence of lightning, the Catenary System (used to protect the Space Shuttle) can be used but would be very costly. Sandia National Laboratories (SNL) recommends a less costly (but equally effective) alternative. SNL recommends installing a ground ring complemented with ground rods and radials.

Fluke 1625-2 GEO Earth Ground Tester

Ensuring reliable lightning protection

The presence of sparks in the incident at BWI indicate a lack of equipotentiality. This problem can be identified with a ground resistance tester like the Fluke 1625-2 GEO Earth Ground Tester and other Fluke test tools.

These are the three steps to take to ensure reliable lightning protection:

Step 1. Assess existing grounding system, measure soil resistivity

  • Measure soil resistivity in different areas and soil layers with the Fluke 1625-2 to identify the optimum low-resistive soil area in which to extend the grounding system.
  • Use the resistivity values of different soil layers to determine the type of electrode to use and the depth it should be buried to obtain a lower ground resistance value.

Step 2. Measure ground impedance and continuity, and take other preventive maintenance steps

Fluke Ti400 Infrared Camera
Fluke Ti400 Infrared Camera
Fluke 1587 Insulation Multimeter
Fluke 1587 Insulation Multimeter
  • After the grounding system has been improved based on the measurements in Step 1, measure ground impedance with the 1625-2. This value is very important because lightning is a high frequency event and the ground impedance measurement will help to determine the grounding system's ability to properly dissipate the energy from lightning.
  • Measure continuity of the lightning protection system Down Conductor. This will determine whether the Down Conductor is at the same potential as the other components of the electrical system. All components need to be at the same potential during a lightning event to avoid catastrophic damage.
  • Determine the equipotentiality of all grounding system components by using the 1625-2 to measure either dc resistance or ac resistance between components in the:
    • Lightning Protection System
    • Grounding Electrode System
    • Bonding System (Safety Grounding Conductor/Equipment Grounding Conductor)
    • electronic equipment shielding (Approach and Navigation System)
    • Weather and Airport Advisory Systems (including RVE, ATIS, AWOS, and related systems)
  • Install a surge suppressor with adequate current capacity per IEEEC.62.41 to protect electronic equipment.

Step 3. Troubleshoot problems

  • Identify loose connections and overheated transformers and conductors using the 1625-2 to measure resistance values or the difference in potential between two points. You can also use an infrared camera such as the Fluke Ti400 to show temperature differences between components.
  • Identify insulation breakdown by measuring insulation resistance with the Fluke 1587 Insulation Multimeter.

Learn more

Welcome to Fluke's Chat GPT Assistant. As with other generative AI systems, this chatbot may occasionally generate incorrect information. For questions regarding the safe use of Fluke tools, please refer to your owners manual. You must comply with your employer’s safety standards and obtain necessary training before using Fluke tools or taking electrical measurements. To speak with a person, visit our Contact Us page.