Maintaining Backup Battery Systems for Maximum Usage and Reliability

Standby battery backup systems play a critical role in keeping essential operations functional in the event of a utility outage.

March 2015

Facilities like data centers, hospitals, airports, utilities, oil and gas facilities, and railways can’t operate without 100 percent backup power reliability. Even standard commercial and manufacturing facilities have backup power systems for their emergency systems, alarms and controls, emergency lighting, steam and fir control systems.

Most backup power systems use an uninterruptable power supply (UPS) and a string of batteries. The UPS backs up the digital control system (DCS) to keep control of plant operations until systems can be safely shut down or until the auxiliary generator kicks on.

Although most batteries used in modern day UPS systems are “maintenance free,” they are still susceptible to deterioration from corrosion, internal shorts, sulphation, dry-out, and seal failure. This article outlines best practices for keeping these “battery banks” at optimum performance, so that if an outage does occur, the backup is ready.

Top two indicators of battery health

One: Internal battery resistance

Internal resistance is a life-span test, not a capacity test. Battery resistance stays relatively flat up until the end of life draws near. At that point, internal resistance increases and battery capacity decreases. Measuring and tracking this value helps identify when a battery needs replacing.

Fluke 500 Series Battery Analyzer

Measuring ohmic values in sequence mode with a Fluke 500 Series Battery Analyzer

Only use a specialized battery tester designed to measure battery resistance while the battery is in service. Read the voltage drop on the load current (conductance) or the AC impedance. Both results will be in ohmic values.

A single ohmic measurement is of little value without context. Best practice requires measuring ohmic values over months and years, each time comparing them to previous values on record to create a base line.

Two: Discharge testing

Discharge testing is the ultimate way to discover the true available capacity of a battery, but can be complicated to perform. In discharge testing, a battery is connected to a load and discharged over a specified period of time. During this test period, current is regulated and a constant known current is drawn while voltage is measured periodically. Details of the discharge current, the specified time period for discharge testing, and the capacity of the battery in ampere hours can be calculated and compared to the manufacturers’ specification. For example, a 12V 100 amp hour battery may require a discharge current of 12A for an eight hour period. A 12V battery would be considered to be discharged when the terminal voltage is 10.5V.

Batteries cannot support critical loads during and immediately after a discharge test. Transfer critical loads to a different battery bank until well after the test is complete and then reconnect a temporary comparably-sized load to the batteries under test. In addition, before conducting the test, prepare a cooling system to compensate for a rise in ambient temperature. When large batteries discharge, they release a significant amount of energy expended as heat.

Healthy batteries should maintain a capacity above 90% of the manufacturer’s rating; most manufacturers recommend replacing the battery if it falls below 80%. When conducting battery tests, look for these indicators of failure:

  • Drop in capacity of more than 10% compared to the baseline or previous measurement
  • 20% or more increase in impedance compared to baseline or previous
  • Sustained high temperatures, compared to baseline and manufacturer’s specs
  • Degradation in plate condition

How to conduct standard battery tests

Float voltage

  1. Isolate the battery or batteries from the charging system and the load.
  2. Measure the individual cell voltage or string using a digital multimeter or battery analyzer such as on a monthly basis.

Charger output

  1. Measure the charger output voltage at the charger output terminals using a digital multimeter or battery analyzer such as the BT500 series on a monthly basis.
  2. Observe the output current shown on the charger current meter or use an appropriate dc current clamp meter. Measure monthly.

DC float current

  1. Refer to manufacturers specifications for approximate values for expected float currents
  2. Use an appropriate dc current clamp meter to measure expected float current on a monthly basis.

Internal ohmic values

  1. Use a battery analyzer such as the Fluke 500 Series to measure the individual battery ohmic values on a quarterly basis.
  2. Establish reference values and maintain in the battery database.

Top 5 causes of battery failure

  1. Loose terminals and inter-cell connections
  2. Aging
  3. Over-charging and over-discharging
  4. Thermal runaway¹
  5. Ripple

Weakest link

When one battery in a string fails, the entire string

  • goes offline
  • shortens lifespan²

Worst case

A battery with a high level of impedance can overheat and ignite or explode during discharge. Voltage measurements alone will not flat this danger.

¹The main cause of battery failure is heat. For every 8 °C (15 °F) increase in average temperature battery life is cut in half.

²A single bad battery raises the charge voltage of adjacent batteries, due to charger settings, affecting the usable life of the entire string.

Common battery terms

Capacity test: a discharge of a battery at a constant current or a constant power to a specified voltage.

Float current: the current that flows while the batter is held at the float voltage.

Internal Ohmic values: the internal resistance of the battery (a characteristic of every battery).

Discharge testing: the battery is connected to a load until the battery voltage falls below a defined present limit.

AC ripple current: residual ac on the rectified voltage in dc charging and inverter circuits.